Brassy I don't think I've ever had my system (also 5kW hybrid) fail to recover after a power cut.
It's interesting that it didn't record any grid import when there surely must have been. I wonder if the little meter that monitors the CT clamp had failed in some way. Could any of the RCDs have tripped, and then got reset as part of your shutdown/powerup sequence ?
The solar and battery power seem to be very roughly just enough to cover the power consumption of the inverter and bms respectively. Almost as if not only can it not send power to the (full) battery, but it also cannot (must not ?) export, and so had to fully curtail generation. I believe it is a safety requirement that it stop generating AC during a power cut, since that could potentially impact engineers working on the cables outside.
Oh - one thought - it probably has to stop generating if grid voltage or frequency are out of spec. I wonder if the power was sort-of back, but it wasn't "clean" in some sense.
Were there any notifications on the portal ?
Probably have to contact GE support to see if they can find out more about what happened.
(On clipping, there are various strategies for avoiding clipping, but it primarily comes down to ensuring there's space in the battery to accept excess PV power. A forum search should find more, if you are interested.)