Is my inverter correctly limiting output?

5 comments started 2024-06-27 last 2024-06-28
GivEnergy ProductsHybrid
R
#1 rjp

Gen 2, 3.6KW with 9.5 battery, 4.7KW array.

First, the portal reports the inverter as "GIV-HY5.0" which I thought was a known bug but not concerning.

Second, on rare times when the array is maxing out, we see inverter power and grid export significantly over 3.6KW


I'm a bit concerned as the system's on a circuit with a 16A breaker,

G
#2 geoffreycoan

This very much looks like your installer has configured your inverter as a G99 which is a 5kW inverter, not a G98 which is 3.6kW. All of the inverters are 5kW internally its a software setting to change the different mode.

One advantage to you is that you won't get solar clipping that you would otherwise get with a 3.6kW inverter.

There is some tolerance in the breaker trip level, they don't trip at precisely 16A. You should be OK but it would be better if the breaker was a higher rating.

Separately is the question of what your DNO approval was.

GivEnergy Support or your installer can change this setting if you ask them to.

R
#3 rjp

geoffreycoan
Thanks. We went for G98 as a 5KW would have involved replacing the entire feed from the house MCB to the detached garage about 30M away (and buried). A Breaker change is the least of it!

I'll contact support 🙂

R
#4 rjp

geoffreycoan
Sorted 🙂

Seems daft asking them to restrict the power we're generating, but it's preferable to the whole thing tripping out or overloading the AC wiring.

G
#5 geoffreycoan

Glad its sorted for you 👍