#1 Marren2016

I have a couple of 200w panels in the garden I use to charge a bluetti ac180 battery. I'm wondering if I can wire them into my Gen 1 3.6kw GE inverter but the cable would be about 40m in total length.
Would I be wasting my time? I've never seen the panels output more than 260w. What would the volt drop be for something that long?

M
#2 mrand31

With normal 4mm2 cable, you'll lose about .55V for every 10m of total length at 10A, which is a typical full load current.
Given that solar panels work in a 'constant current' mode in normal usage that loss would be trivial.

A more significant problem will be that the gen 1 inverter won't start using solar power before it sees about 150V from the panels. That usually needs four panels minimum.

M
#3 Marren2016

Perfect reply, thank you.

G
#4 geoffreycoan

mrand31 I think there is a minimum voltage setting that Givenergy support can set on the inverter, but 4 panels is the typical recommendation IIRC. There have been other people on the forum with issues with small numbers of panels on a string and the inverter doesn’t respond until its pretty full sun

V
#5 Vestas

geoffreycoan 120V is the minimum startup voltage but that register isn't exposed so you need installer (engineer) access to change it.