I have just had a Solar Panel / Hybrid Inverter / Battery system installed. However, it has not been behaving correctly. Most of the time Load Power shows as 0W, even if I put the kettle on. The PV Power and Battery Power / Percentage graphs seem fine. However, Grid Import / Export / Load are not correct. Periodically the Load "appears" to jump from zero to a high value (e.g. 6KW) along with Grid Import (e.g. -2.9KW) and Battery Power (e.g. 2.6KW).
At first I thought there must be some "real" load on the system, so I isolated everything else in the house, but it still occurred periodically.
After reading other discussions on the forum my theory is that the CT Clamp has been fitted the wrong way around and so the Import / Export / Load figures are invalid / reversed.
Does this theory sound reasonable to others with more experience ?
Is there any GivEnergy Inverter configuration that I could apply to compensate for the reverse fitting of the CT Clamp ? - this would be a temporary solution to test the theory, ahead of the installers correcting the problem
Any feedback would be appreciated