Pete Thomas All the inverter is doing is generating AC, which goes onto the house wiring. If that exceeds the house consumption, the excess goes to the grid. If that is not enough to cover the house consumption, it will have to import to make up the difference.
I consider it a missing feature that there isn't a mode where you discharge to the grid, but can increase the discharge if consumption goes up. Currently, you are either in eco, which tries to have 0 import/export, or you discharge at a fixed power, which may or may not be enough to cover house demand. So eg, if you are discharging at 1kW, but then put the kettle on, you'll probably have to start importing 2kW.
I suggested a way to add a bias to eco mode, so that it would try to discharge a minimum power. Eg rather than trying to keep grid usage at 0, it would try to keep it at 1kW export. Then if you put the kettle on, it will try to generate 4kW (or as much as it can) to cover increase consumption but still try to be exporting. But that was rejected.