Today around 09:33 we had our first power outage since firmware upgrade of our All-in-One
The outage was brief, but it was a disconcerting experience of the "whole house backup".

I'd be interested to know if what follows is the expected behaviour of the system.
FYI I have a SolarEdge SE5000H ac coupled. Sunny morning, battery over 90%
I was certainly not expecting lights to go out, computers to reboot and TV to switch off, however briefly the interruption to grid.
Looking at the logs, Inverter Data shows the frequency bumps up to 54Hz

This appears to switch off the SE5000H but recovers after about a minute

The PV generation being switched off is not unexpected as we don't want any chance of grid export during a grid fault.
What I did not expect is that the house load (around 0.5 kW) was not immediately supplied by the battery.
The evidence from the logs is that following the brief grid interruption, the house load was supplied by the grid for at least 30 seconds, before the PV inverter recovered.
PV subsequently carried on charging the battery and supplying the house load.

But I was under the imperession the house should have gone into an island mode protecting the house from the grid failure.
I have no idea if this is a faulty installation or some new behaviour of recent firmware upgrade.