#1 Mrfish

Hi
I’m having a bit of a problem
I’ve a 3.6kwh gen 1 inverter, when I set the batteries to TIMED EXPORT the ECO disables itself, meaning I then instantly draw from the grid
I’m having to do it manually, so disable the export and then enable ECO
Software version is up to date
any ideas please?

D
#2 DD

Mrfish yes, it seems to be a feature of the gen-1 inverter that eco must be turned off in order to force an export. And I think the software helpfully turns eco off when configure a timed export.

Some newer releases of the gen-1 do have newer firmware which does behave better, but I'm not sure if that's generally available.

You may need to use some external software. There are a number of options.

See https://community.givenergy.cloud/d/5221-app-for-setting-multiple-charge-periods
(Charging schedulers can also sort out exports.)

R
#3 Rbor

Mrfish I have AC3.0 (2022) and have same issue if I use GE's method of setting up Eco, Export, etc.
In Summer 2023, I was on Flux and I always used the 4-7pm slot to export (really good rates). But every day, I set an alarm/reminder just before 7 pm to alert me to switching Eco back on.
Some people have set up automations.

Since Jan 2024, I have been on Predbat and Agile import which does all this for me automatically. So I never use the GE method now.

Rob