Hi all,
After some issues with a cell on battery no.3 (all of these are a single 9.5kWh gen 2, with a 5kW hybrid inverter), GE sent out at engineer last week to have a look at it. I don't know how much troubleshooting was attempted (I was stuck in Teams meetings, otherwise would have hovered annoyingly over his shoulder out of curiosity), but he ended up just swapping out the whole thing for a replacement unit before heading back down the road. He said it didn't need recalibration as it had been done before leaving base.
After sorting out the home assistant entities, I had a bit of a look at it: unlike previous replacements, this one appears to be a refurb, with around 500 cycles to its name. This does not seem unreasonable, as the old one had something like 7-800 cycles under its belt, but would have been nice if he had mentioned this. Capacity was showing as a suspiciously precise 186.0 Ah.
After a couple of days use I checked on the input/output totals, and it looks like I'm only able to put 7.5 - 8 kWh into it. Ran a couple of calibrations, shown below, once at full rate down / half rate up (poor solar day), followed by another at half rate each direction.
New capacity reading: 158.8 kWh, or about 85% nominal capacity.

From a look at the cell voltages, battery no.4 is generally looking better than battery no.3, which had one cell deviating from the others even under very low rate charging. Here, all the cells stay together remarkably well, except for that obvious big drop on cell 1 at low voltage. This is obviously restricting the low end of the range.

So, what do we think? Back on the phone again? Getting a bit tired of the sheer length of time it takes anything to happen. It's partly just the nature of systems like this which operate on the scale of hours, but the inevitable "problems only identifiable hours/days after the engineer has left" are rather frustrating.