So I replicated a power cut again to test if my RCDs worked when in ‘island mode”.
On isolating the grid, some flicker occurred on an LED bulb but everything else changed over seamlessly – modem, router, cooker clocks etc all continued without interruption and neither of my Type A nor Type AC RCDs tripped. Everything was working fine.
I then tested if the RCDs would trip by using a cheap socket tester I have which has the facility to provoke a RCD test. I have 3 ring mains and on plugging into each circuit the tester indicated a fault, that each circuit had a Live Neutral reverse! I tried to provoke a trip of the RCD but could not using the socket tester. I then tested each of the RCDs by pressing the test button each and both tripped. Both were able to be reset without any problem.
On restoring the grid power, everything changed over fine. Then, about 10 seconds later the PV breaker in the Gateway switched itself off. It reset without a problem.
Now that the grid was restored, I checked each of the ring mains again and now the tester indicated they were all working fine. I was also able to trip the RCDs by the test function on the socket tester.
So, in summary, all functionality remained when in island mode – nothing tripped, everything worked. However, the cheap socket tester indicated a Live Neutral reverse and a RCD trip could not be provoked by the tester when in island mode. My circuits have been successfully tested in past and don't have a "real" Live Neutral reverse hence the reason for this indicated fault is beyond my knowledge but for now I’m guessing it is due to how island mode produces 120v live to -120v neutral???
Another question is are the RCDs (of any type) still fully functional under this type of operation?
The reason for the PV breaker trip also needs to be explained.
I’d like to understand some more before I ask my installer/GE for advice. Grateful for any comments from others.